我在使用SCI的EX!後,想加入一個EPWM在PWM2A,也已經將設定調整至與成功過的專案一樣,但無法成功,以下是程式.c以及board.c
// FILE: sci_ex1_loopback.c
// TITLE: SCI FIFO Digital Loop Back.
//! \addtogroup driver_example_list
//! <h1>SCI FIFO Digital Loop Back</h1>
//! This program uses the internal loop back test mode of the peripheral.
//! Other then boot mode pin configuration, no other hardware configuration
//! is required. The pinmux and SCI modules are configured through the
//! sysconfig file.
//! This test uses the loopback test mode of the SCI module to send
//! characters starting with 0x00 through 0xFF. The test will send
//! a character and then check the receive buffer for a correct match.
//! \note This example project has support for migration across our C2000
//! device families. If you are wanting to build this project from launchpad
//! or controlCARD, please specify in the .syscfg file the board you're using.
//! At any time you can select another device to migrate this example.
//! \b Watch \b Variables \n
//! - \b loopCount - Number of characters sent
//! - \b errorCount - Number of errors detected
//! - \b sendChar - Character sent
//! - \b receivedChar - Character received
// C2000Ware v5.04.00.00
// Copyright (C) 2024 Texas Instruments Incorporated - http://www.ti.com
// Redistribution and use in source and binary forms, with or without
// modification, are permitted provided that the following conditions
// are met:
// Redistributions of source code must retain the above copyright
// notice, this list of conditions and the following disclaimer.
// Redistributions in binary form must reproduce the above copyright
// notice, this list of conditions and the following disclaimer in the
// documentation and/or other materials provided with the
// distribution.
// Neither the name of Texas Instruments Incorporated nor the names of
// its contributors may be used to endorse or promote products derived
// from this software without specific prior written permission.
// THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS
// "AS IS" AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT
// LIMITED TO, THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS FOR
// A PARTICULAR PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE COPYRIGHT
// OWNER OR CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT, INCIDENTAL,
// SPECIAL, EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING, BUT NOT
// LIMITED TO, PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES; LOSS OF USE,
// DATA, OR PROFITS; OR BUSINESS INTERRUPTION) HOWEVER CAUSED AND ON ANY
// THEORY OF LIABILITY, WHETHER IN CONTRACT, STRICT LIABILITY, OR TORT
// (INCLUDING NEGLIGENCE OR OTHERWISE) ARISING IN ANY WAY OUT OF THE USE
// OF THIS SOFTWARE, EVEN IF ADVISED OF THE POSSIBILITY OF SUCH DAMAGE.
// Included Files
#include "driverlib.h"
#include "device.h"
#include "board.h"
// Globals
uint16_t loopCount;
uint16_t errorCount;
// Function Prototypes
void error();
// Main
void main(void)
uint16_t sendChar;
uint16_t receivedChar;
// Initialize device clock and peripherals
Device_init();
// Setup GPIO by disabling pin locks and enabling pullups
Device_initGPIO();
// Initialize PIE and clear PIE registers. Disables CPU interrupts.
Interrupt_initModule();
// Initialize the PIE vector table with pointers to the shell Interrupt
// Service Routines (ISR).
Interrupt_initVectorTable();
// Board Initialization
Board_init();
EINT;
ERTM;
// Enables CPU interrupts
Interrupt_enableGlobal();
// Initialize counts
loopCount = 0;
errorCount = 0;
// Send a character starting with 0
sendChar = 0;
// Send Characters forever starting with 0x00 and going through 0xFF.
// After sending each, check the receive buffer for the correct value.
while(1)
SCI_writeCharNonBlocking(mySCI0_BASE, sendChar);
// Wait for RRDY/RXFFST = 1 for 1 data available in FIFO
while(SCI_getRxFIFOStatus(mySCI0_BASE) == SCI_FIFO_RX0)
// Check received character
receivedChar = SCI_readCharBlockingFIFO(mySCI0_BASE);
// Received character not correct
if(receivedChar != sendChar)
errorCount++;
// asm(" ESTOP0"); // Uncomment to stop the test here
for (;;);
// Move to the next character and repeat the test
sendChar++;
// Limit the character to 8-bits
sendChar &= 0x00FF;
loopCount++;
DEVICE_DELAY_US(50000);
// End of file
//=============================================board.c==============================================
* Copyright (c) 2020 Texas Instruments Incorporated - http://www.ti.com
* All rights reserved.
* Redistribution and use in source and binary forms, with or without
* modification, are permitted provided that the following conditions
* are met:
* * Redistributions of source code must retain the above copyright
* notice, this list of conditions and the following disclaimer.
* * Redistributions in binary form must reproduce the above copyright
* notice, this list of conditions and the following disclaimer in the
* documentation and/or other materials provided with the distribution.
* * Neither the name of Texas Instruments Incorporated nor the names of
* its contributors may be used to endorse or promote products derived
* from this software without specific prior written permission.
* THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS "AS IS"
* AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT LIMITED TO,
* THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS FOR A PARTICULAR
* PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE COPYRIGHT OWNER OR
* CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT, INCIDENTAL, SPECIAL,
* EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING, BUT NOT LIMITED TO,
* PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES; LOSS OF USE, DATA, OR PROFITS;
* OR BUSINESS INTERRUPTION) HOWEVER CAUSED AND ON ANY THEORY OF LIABILITY,
* WHETHER IN CONTRACT, STRICT LIABILITY, OR TORT (INCLUDING NEGLIGENCE OR
* OTHERWISE) ARISING IN ANY WAY OUT OF THE USE OF THIS SOFTWARE,
* EVEN IF ADVISED OF THE POSSIBILITY OF SUCH DAMAGE.
#include "board.h"
// Board Configurations
// Initializes the rest of the modules.
// Call this function in your application if you wish to do all module
// initialization.
// If you wish to not use some of the initializations, instead of the
// Board_init use the individual Module_inits
void Board_init()
EALLOW;
PinMux_init();
SYSCTL_init();
SYNC_init();
ASYSCTL_init();
MEMCFG_init();
DAC_init();
EPWM_init();
SCI_init();
EDIS;
// PINMUX Configurations
void PinMux_init()
// PinMux for modules assigned to CPU1
// ANALOG -> myANALOGPinMux0 Pinmux
// Analog PinMux for A0, B15, C15, DACA_OUT
GPIO_setPinConfig(GPIO_231_GPIO231);
// AIO -> Analog mode selected
GPIO_setAnalogMode(231, GPIO_ANALOG_ENABLED);
// EPWM2 -> myEPWM2 Pinmux
GPIO_setPinConfig(myEPWM2_EPWMA_PIN_CONFIG);
GPIO_setPadConfig(myEPWM2_EPWMA_GPIO, GPIO_PIN_TYPE_STD);
GPIO_setQualificationMode(myEPWM2_EPWMA_GPIO, GPIO_QUAL_SYNC);
GPIO_setPinConfig(myEPWM2_EPWMB_PIN_CONFIG);
GPIO_setPadConfig(myEPWM2_EPWMB_GPIO, GPIO_PIN_TYPE_STD);
GPIO_setQualificationMode(myEPWM2_EPWMB_GPIO, GPIO_QUAL_SYNC);
// SCIA -> mySCI0 Pinmux
GPIO_setPinConfig(mySCI0_SCIRX_PIN_CONFIG);
// AGPIO -> GPIO mode selected
GPIO_setAnalogMode(28, GPIO_ANALOG_DISABLED);
GPIO_setPadConfig(mySCI0_SCIRX_GPIO, GPIO_PIN_TYPE_STD | GPIO_PIN_TYPE_PULLUP);
GPIO_setQualificationMode(mySCI0_SCIRX_GPIO, GPIO_QUAL_ASYNC);
GPIO_setPinConfig(mySCI0_SCITX_PIN_CONFIG);
GPIO_setPadConfig(mySCI0_SCITX_GPIO, GPIO_PIN_TYPE_STD | GPIO_PIN_TYPE_PULLUP);
GPIO_setQualificationMode(mySCI0_SCITX_GPIO, GPIO_QUAL_ASYNC);
// ASYSCTL Configurations
void ASYSCTL_init(){
// asysctl initialization
// Disables the temperature sensor output to the ADC.
ASysCtl_disableTemperatureSensor();
// Set the analog voltage reference selection to external.
ASysCtl_setAnalogReferenceExternal( ASYSCTL_ANAREF_VREFHI_ADCA | ASYSCTL_ANAREF_VREFHI_ADCB | ASYSCTL_ANAREF_VREFHI_ADCC | ASYSCTL_ANAREF_VREFHI_ADCD | ASYSCTL_ANAREF_VREFHI_ADCE );
// DAC Configurations
void DAC_init(){
myDAC0_init();
void myDAC0_init(){
// Set DAC reference voltage.
DAC_setReferenceVoltage(myDAC0_BASE, DAC_REF_ADC_VREFHI);
// Set DAC gain mode.
DAC_setGainMode(myDAC0_BASE, DAC_GAIN_ONE);
// Set DAC load mode.
DAC_setLoadMode(myDAC0_BASE, DAC_LOAD_SYSCLK);
// Enable the DAC output
DAC_enableOutput(myDAC0_BASE);
// Set the DAC shadow output
DAC_setShadowValue(myDAC0_BASE, 2048U);
// Delay for buffered DAC to power up.
DEVICE_DELAY_US(500);
// EPWM Configurations
void EPWM_init(){
EPWM_setClockPrescaler(myEPWM2_BASE, EPWM_CLOCK_DIVIDER_1, EPWM_HSCLOCK_DIVIDER_2);
EPWM_setTimeBasePeriod(myEPWM2_BASE, 7500);
EPWM_enableGlobalLoadRegisters(myEPWM2_BASE, EPWM_GL_REGISTER_TBPRD_TBPRDHR);
EPWM_setTimeBaseCounter(myEPWM2_BASE, 0);
EPWM_setTimeBaseCounterMode(myEPWM2_BASE, EPWM_COUNTER_MODE_UP);
EPWM_disablePhaseShiftLoad(myEPWM2_BASE);
EPWM_setPhaseShift(myEPWM2_BASE, 0);
EPWM_setSyncInPulseSource(myEPWM2_BASE, EPWM_SYNC_IN_PULSE_SRC_DISABLE);
EPWM_setCounterCompareValue(myEPWM2_BASE, EPWM_COUNTER_COMPARE_A, 3750);
EPWM_enableGlobalLoadRegisters(myEPWM2_BASE, EPWM_GL_REGISTER_CMPA_CMPAHR);
EPWM_setCounterCompareShadowLoadMode(myEPWM2_BASE, EPWM_COUNTER_COMPARE_A, EPWM_COMP_LOAD_ON_CNTR_ZERO);
EPWM_setCounterCompareValue(myEPWM2_BASE, EPWM_COUNTER_COMPARE_B, 0);
EPWM_setCounterCompareShadowLoadMode(myEPWM2_BASE, EPWM_COUNTER_COMPARE_B, EPWM_COMP_LOAD_ON_CNTR_ZERO);
EPWM_setActionQualifierAction(myEPWM2_BASE, EPWM_AQ_OUTPUT_A, EPWM_AQ_OUTPUT_HIGH, EPWM_AQ_OUTPUT_ON_TIMEBASE_ZERO);
EPWM_setActionQualifierAction(myEPWM2_BASE, EPWM_AQ_OUTPUT_A, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_PERIOD);
EPWM_setActionQualifierAction(myEPWM2_BASE, EPWM_AQ_OUTPUT_A, EPWM_AQ_OUTPUT_LOW, EPWM_AQ_OUTPUT_ON_TIMEBASE_UP_CMPA);
EPWM_setActionQualifierAction(myEPWM2_BASE, EPWM_AQ_OUTPUT_A, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_DOWN_CMPA);
EPWM_setActionQualifierAction(myEPWM2_BASE, EPWM_AQ_OUTPUT_A, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_UP_CMPB);
EPWM_setActionQualifierAction(myEPWM2_BASE, EPWM_AQ_OUTPUT_A, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_DOWN_CMPB);
EPWM_setActionQualifierAction(myEPWM2_BASE, EPWM_AQ_OUTPUT_B, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_ZERO);
EPWM_setActionQualifierAction(myEPWM2_BASE, EPWM_AQ_OUTPUT_B, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_PERIOD);
EPWM_setActionQualifierAction(myEPWM2_BASE, EPWM_AQ_OUTPUT_B, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_UP_CMPA);
EPWM_setActionQualifierAction(myEPWM2_BASE, EPWM_AQ_OUTPUT_B, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_DOWN_CMPA);
EPWM_setActionQualifierAction(myEPWM2_BASE, EPWM_AQ_OUTPUT_B, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_UP_CMPB);
EPWM_setActionQualifierAction(myEPWM2_BASE, EPWM_AQ_OUTPUT_B, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_DOWN_CMPB);
EPWM_setRisingEdgeDelayCountShadowLoadMode(myEPWM2_BASE, EPWM_RED_LOAD_ON_CNTR_ZERO);
EPWM_disableRisingEdgeDelayCountShadowLoadMode(myEPWM2_BASE);
EPWM_setFallingEdgeDelayCountShadowLoadMode(myEPWM2_BASE, EPWM_FED_LOAD_ON_CNTR_ZERO);
EPWM_disableFallingEdgeDelayCountShadowLoadMode(myEPWM2_BASE);
EPWM_enableADCTrigger(myEPWM2_BASE, EPWM_SOC_A);
EPWM_setADCTriggerSource(myEPWM2_BASE, EPWM_SOC_A, EPWM_SOC_TBCTR_ZERO);
EPWM_setADCTriggerEventPrescale(myEPWM2_BASE, EPWM_SOC_A, 1);
// MEMCFG Configurations
void MEMCFG_init(){
// Initialize RAMs
// Configure LSRAMs
MemCfg_setLSRAMControllerSel(MEMCFG_SECT_LS0, MEMCFG_LSRAMCONTROLLER_CPU_ONLY);
MemCfg_setLSRAMControllerSel(MEMCFG_SECT_LS1, MEMCFG_LSRAMCONTROLLER_CPU_ONLY);
MemCfg_setLSRAMControllerSel(MEMCFG_SECT_LS2, MEMCFG_LSRAMCONTROLLER_CPU_ONLY);
MemCfg_setLSRAMControllerSel(MEMCFG_SECT_LS3, MEMCFG_LSRAMCONTROLLER_CPU_ONLY);
MemCfg_setLSRAMControllerSel(MEMCFG_SECT_LS4, MEMCFG_LSRAMCONTROLLER_CPU_ONLY);
MemCfg_setLSRAMControllerSel(MEMCFG_SECT_LS5, MEMCFG_LSRAMCONTROLLER_CPU_ONLY);
MemCfg_setLSRAMControllerSel(MEMCFG_SECT_LS6, MEMCFG_LSRAMCONTROLLER_CPU_ONLY);
MemCfg_setLSRAMControllerSel(MEMCFG_SECT_LS7, MEMCFG_LSRAMCONTROLLER_CPU_ONLY);
MemCfg_setLSRAMControllerSel(MEMCFG_SECT_LS8, MEMCFG_LSRAMCONTROLLER_CPU_ONLY);
MemCfg_setLSRAMControllerSel(MEMCFG_SECT_LS9, MEMCFG_LSRAMCONTROLLER_CPU_ONLY);
// Configure GSRAMs
// Configure Access Protection for RAMs
MemCfg_setProtection(MEMCFG_SECT_M0, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE);
MemCfg_setProtection(MEMCFG_SECT_M1, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE);
MemCfg_setProtection(MEMCFG_SECT_LS0, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE);
MemCfg_setProtection(MEMCFG_SECT_LS1, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE);
MemCfg_setProtection(MEMCFG_SECT_LS2, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE);
MemCfg_setProtection(MEMCFG_SECT_LS3, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE);
MemCfg_setProtection(MEMCFG_SECT_LS4, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE);
MemCfg_setProtection(MEMCFG_SECT_LS5, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE);
MemCfg_setProtection(MEMCFG_SECT_LS6, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE);
MemCfg_setProtection(MEMCFG_SECT_LS7, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE);
MemCfg_setProtection(MEMCFG_SECT_LS8, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE);
MemCfg_setProtection(MEMCFG_SECT_LS9, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE);
MemCfg_setProtection(MEMCFG_SECT_GS0, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE | MEMCFG_PROT_ALLOWDMAWRITE);
MemCfg_setProtection(MEMCFG_SECT_GS1, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE | MEMCFG_PROT_ALLOWDMAWRITE);
MemCfg_setProtection(MEMCFG_SECT_GS2, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE | MEMCFG_PROT_ALLOWDMAWRITE);
MemCfg_setProtection(MEMCFG_SECT_GS3, MEMCFG_PROT_ALLOWCPUFETCH | MEMCFG_PROT_ALLOWCPUWRITE | MEMCFG_PROT_ALLOWDMAWRITE);
// Lock/Commit Registers
// Enable Access Violation Interrupt
// Correctable error Interrupt
MemCfg_setCorrErrorThreshold(0);
MemCfg_disableCorrErrorInterrupt(MEMCFG_CERR_CPUREAD);
// SCI Configurations
void SCI_init(){
mySCI0_init();
void mySCI0_init(){
SCI_clearInterruptStatus(mySCI0_BASE, SCI_INT_RXFF | SCI_INT_TXFF | SCI_INT_FE | SCI_INT_OE | SCI_INT_PE | SCI_INT_RXERR | SCI_INT_RXRDY_BRKDT | SCI_INT_TXRDY);
SCI_clearOverflowStatus(mySCI0_BASE);
SCI_resetTxFIFO(mySCI0_BASE);
SCI_resetRxFIFO(mySCI0_BASE);
SCI_resetChannels(mySCI0_BASE);
SCI_setConfig(mySCI0_BASE, DEVICE_LSPCLK_FREQ, mySCI0_BAUDRATE, (SCI_CONFIG_WLEN_8|SCI_CONFIG_STOP_ONE|SCI_CONFIG_PAR_NONE));
SCI_enableLoopback(mySCI0_BASE);
SCI_performSoftwareReset(mySCI0_BASE);
SCI_setFIFOInterruptLevel(mySCI0_BASE, SCI_FIFO_TX0, SCI_FIFO_RX0);
SCI_enableFIFO(mySCI0_BASE);
SCI_enableModule(mySCI0_BASE);
// SYNC Scheme Configurations
void SYNC_init(){
SysCtl_setSyncOutputConfig(SYSCTL_SYNC_OUT_SRC_EPWM1SYNCOUT);
// SOCA
SysCtl_enableExtADCSOCSource(0);
// SOCB
// SYSCTL Configurations
void SYSCTL_init(){
// sysctl initialization
SysCtl_setStandbyQualificationPeriod(2);
SysCtl_configureType(SYSCTL_USBTYPE, 0, 0);
SysCtl_configureType(SYSCTL_ECAPTYPE, 0, 0);
SysCtl_selectErrPinPolarity(0);
SysCtl_disableMCD();
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_ADCA,
SYSCTL_ACCESS_CPU1, SYSCTL_ACCESS_FULL);
SYSCTL_ACCESS_CLA1, SYSCTL_ACCESS_FULL);
SYSCTL_ACCESS_DMA1, SYSCTL_ACCESS_FULL);
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_ADCB,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_ADCC,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_ADCD,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_ADCE,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_CMPSS1,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_CMPSS2,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_CMPSS3,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_CMPSS4,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_DACA,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_PGA1,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_PGA2,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_PGA3,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EPWM1,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EPWM2,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EPWM3,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EPWM4,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EPWM5,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EPWM6,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EPWM7,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EPWM8,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EPWM9,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EPWM10,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EPWM11,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EPWM12,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EQEP1,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EQEP2,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_EQEP3,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_ECAP1,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_ECAP2,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_CLB1,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_CLB2,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_SCIA,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_SCIB,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_SCIC,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_SPIA,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_SPIB,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_I2CA,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_I2CB,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_PMBUSA,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_LINA,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_MCANA,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_MCANB,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_FSIATX,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_FSIARX,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_USBA,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_HRPWMA,
SysCtl_setPeripheralAccessControl(SYSCTL_ACCESS_AESA,
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_CLA1);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_DMA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_TIMER0);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_TIMER1);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_TIMER2);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_HRCAL);
SysCtl_disablePeripheral(SYSCTL_PERIPH_CLK_TBCLKSYNC);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_ERAD);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPWM1);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPWM2);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPWM3);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPWM4);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPWM5);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPWM6);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPWM7);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPWM8);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPWM9);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPWM10);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPWM11);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPWM12);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_ECAP1);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_ECAP2);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EQEP1);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EQEP2);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EQEP3);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_SCIA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_SCIB);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_SCIC);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_SPIA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_SPIB);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_I2CA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_I2CB);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_MCANA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_MCANB);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_USBA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_NPU);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_ADCA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_ADCB);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_ADCC);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_ADCD);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_ADCE);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_CMPSS1);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_CMPSS2);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_CMPSS3);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_CMPSS4);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_PGA1);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_PGA2);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_PGA3);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_DACA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_CLB1);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_CLB2);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_FSITXA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_FSIRXA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_LINA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_PMBUSA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_DCC0);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_DCC1);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_AESA);
SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_EPG1);